M

Maestro

was testing portakabin DB today but when dong the RCD trip it keeps taking the RCD supplying the portakabin how do i get around thanks before hand
 
Re: Rcd testing main board supply tripping befroe the sub board how do i get round it

take the RCD out of the cabin if the supply cable needs RCD protection. if it doesn't need it, feed from main DB from a non-RCD way. 2 RCDs in series will give you this problem. bad design.
 
Re: Rcd testing main board supply tripping befroe the sub board how do i get round it

sorry i should have been clearer i am testing the portakabin in a workshop they are just plugged into a 32amp industrial socket which is being fed by a 32amp 30MA RCD
 
Re: Rcd testing main board supply tripping befroe the sub board how do i get round it

Posts #2 and #3 help you then?? Daz
 
Re: Rcd testing main board supply tripping befroe the sub board how do i get round it

Also,if TT to 32 A socket outside,RCD has to be two pole,but as told,fashion supply to test from non-RCD point.....and does it smell like a damp knicker drawer?...the three i was in today did...
 

Reply to Rcd testing main board supply tripping befroe the sub board how do i get round it ? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
655
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
790

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top