RCD testing - metrel MI3000 | on ElectriciansForums

Discuss RCD testing - metrel MI3000 in the UK Electrical Forum area at ElectriciansForums.net

gazdkw82

-
Arms
Joined
Aug 2, 2013
Messages
1,912
Reaction score
880
Location
leicester
Been noticing that when I run an auto RCD test I sometimes get a failure on the x1 and sometimes x1/2. However when performing the tests individually everything is fine.

Has anyone had these issues?
 
Hi, I don’t have your tester so I can’t say about your issue directly. But, perhaps it’s the RCD (?). My thought being that after years of no operation or testing its movement might not be working to spec initially. If I get an auto test fail (rare) I don’t immediately retest. I hit the RCD test button a few times, recheck I’ve picked the right RCD type on the test, then re run.
 
Sorry I meant apart from factors to do with the tester. Brand of RCD, type of RCD, testing from device terminals or down circuit, etc ?

No nothing consistent. Recently had a job where the RCD was tripping at half times on auto test but when I performed the half times on it's own it was fine, no matter what side of the wave. The other day I had the opposite, auto test failed because at x1 the RCD was too slow to trip. Then performed it on it's own at x1 and it was fine.

Tbh both RCD's we're over 10 years old. However still seemed odd
 
Are we not doing an rcd test to prove they react quick enough incase of a fault to earth surley by pressing the test button you have woke it up and now not testing it under realistic fault conditions
Yes, but I don’t think it’s wrong to give it a few warm up stretches. After all, the manufacturer asks for it to be tripped 4 times a year and so if it’s 10 years old that’s 40 it’s probably not had. If it doesn’t trip with the test button then that’s that really.
 
Yes, but I don’t think it’s wrong to give it a few warm up stretches. After all, the manufacturer asks for it to be tripped 4 times a year and so if it’s 10 years old that’s 40 it’s probably not had. If it doesn’t trip with the test button then that’s that really.
4 times thought it was once every 6 months
 

Reply to RCD testing - metrel MI3000 in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
It can also mean lasts or continues for two years.
Replies
14
Views
1K
  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
745

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top