I'm testing an installation and all of the tests have gone well until the RCD rest on the upstairs ringmain.

The ring main itself is a loop of 9 sockets - the phases are a loop, as is the neutral and the cpc, all with suitable continuity resistance. The insulation resistance test is also suitably high.

When I plug in the RCD tester (megger CBT3) the P-N and P-E light up but the screen displays >50v which according to the manual means there is a N-E voltage greater than 50v. So I checked this with a multimeter and there is indeed a voltage present; 230v WTF :shout::shout::shout:

Now this sounds to me like a dicky neutral or earth but I've had the entire ring apart, checked connections, checked for ring again, checked IR again, checked the consumer unit terminations.
I also considered a dodgy tester but it functions for the downstairs ring and kitchen ring so I think I can eliminate that possibility.

Can anyone offer some suggestions?

Thanks
 
i would suspect connections in CU. have you caught the insulation on either the cpc or N? is the busbar properly into the MCB? sometimes it can go behind the clamp and make a poor connection.
 
Do you have anything plugged into the ring that may be faulty and causing the N-PE voltage, thoguh this shoudl have been found on the IR testing?

I would tend toward Tel's response that the fault is at the CU since there seems to be no fault on the ring when it is not connected to the CU.
 
Just a quick one to say I have found the solution, in case anyone else has something similar.

Turns out, the neutral of this circuit went to the wrong RCD neutral bar (split load CU) :38:

May be helpful if someone comes across this.

Thanks all for your suggestions, they were much appreciated.
 
i am with Jason on this, i have never come across (yet) where the neutral incorrectly installed/connected at DB would when tested or put under load fail to trip etc
But glad you go sorted

off topic
I personally prefer individual rcbos when the client dont mind the cost :) (my last 2 big jobs had a total of 163 HAGER rcbos in their 3phase boards)
 
I hate dual RCD boards. Just go for the cheap RCBO boards now

Agree wholeheartedly!! Dual 17th boards as they are called and even the the so called (and ill named) ''high integrity'' dual boards, are nothing more than a compromise, ...A compromise on cost, and a compromise on electrical integrity and safety!! Apart from anything else, they can be a complete pain when trying to locate a fault (especially a leakage fault) on one of the protected circuits.

When all said and done, you can't get a higher integrity in a CU layout, than an all RCBO board!!!
 

Reply to RCD Testing Problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
159
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
526
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
474

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
661
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
610

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top