Hi,
I'm testing an installation and all of the tests have gone well until the RCD rest on the upstairs ringmain.
The ring main itself is a loop of 9 sockets - the phases are a loop, as is the neutral and the cpc, all with suitable continuity resistance. The insulation resistance test is also suitably high.
When I plug in the RCD tester (megger CBT3) the P-N and P-E light up but the screen displays >50v which according to the manual means there is a N-E voltage greater than 50v. So I checked this with a multimeter and there is indeed a voltage present; 230v WTF :shout::shout::shout:
Now this sounds to me like a dicky neutral or earth but I've had the entire ring apart, checked connections, checked for ring again, checked IR again, checked the consumer unit terminations.
I also considered a dodgy tester but it functions for the downstairs ring and kitchen ring so I think I can eliminate that possibility.
Can anyone offer some suggestions?
Thanks
I'm testing an installation and all of the tests have gone well until the RCD rest on the upstairs ringmain.
The ring main itself is a loop of 9 sockets - the phases are a loop, as is the neutral and the cpc, all with suitable continuity resistance. The insulation resistance test is also suitably high.
When I plug in the RCD tester (megger CBT3) the P-N and P-E light up but the screen displays >50v which according to the manual means there is a N-E voltage greater than 50v. So I checked this with a multimeter and there is indeed a voltage present; 230v WTF :shout::shout::shout:
Now this sounds to me like a dicky neutral or earth but I've had the entire ring apart, checked connections, checked for ring again, checked IR again, checked the consumer unit terminations.
I also considered a dodgy tester but it functions for the downstairs ring and kitchen ring so I think I can eliminate that possibility.
Can anyone offer some suggestions?
Thanks