When you have a RCD as a main switch i have allways tested each circuit on the RCD but i got told today that you only need to test the RCD once is this right or am i right??
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss RCD testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
ok so i`m wrong! saves a lot of time thanksThought you just tested at the nearest socket to the board
As everyone's said, only needs doing once. You said when RCD is main switch though, as far as I know RCD can't be used as main isolator under 17th, it needs to be a separate double pole isolator?
RCD as MS is fine so long as its double pole, can take the load and has the required contact seperation...