T

tc50

hello im new here and baffled after today.doing rcd trip times test with newish newlec multifunction tester.new install 0n up and down ring circuits on separate rcds trip x half ok on both trip x 5 ok on both less than 40 m/secs but trip x 1 on both rcds tripped rcds but no readings due to safety cut out on meter indicating 50 v ,have lost manual so not sure what this means but strange on both new circuits and new hlgh integrity board rcds would appreciate any views.
 
if you are testing at the RCD using probes. it could be a momentary bad connection when the RCD trips. try at a socket using the 3 pin plug.
 
its plug in type to sockets on both manual and auto though it might be meter fault but tried it at home all ok could it be an applience plugged in that ive missed unplugging or existing circuits now rcd controlled but had meggered and tested ok
 
thanks by this i presume you mean disconnect all circuits except rings and retest then each circuit individually to trace problem .....bummer looks like i,m working tomorrow then ....for free boo hoo
 
Do not know about The newlec meter but on a Metrel the test button is used as an earth comparison (i.e using you) if you are statically charged then this charge generates a voltage on the meter when you press the test button and the meter sees this as a voltage to earth and causes the meter not to test. If you press the test button through an insulator e.g VDE screwdriver the test works.
 
well you learn something everyday man will try this next time it happens thanks for reply,also would you recommend metrel instruments as i,m looking for a complete new kit of everything at best rates.
 
I have a metrel MI23002 from instrotech and I find it is great. It has rechargeable batteries, a download facility for your data (which is a bit odd but useful) doea ll the tests for PIRs and inital verification and also does phase rotation and RCD ramp test.
It does not do earth leakage current, but I have a multimeter for that, if I ever do it.
Everyone has their own favorites and most love Megger but they are more expensive and this one does all I need. the only problem is the static bit.
 
hello im new here and baffled after today.doing rcd trip times test with newish newlec multifunction tester.new install 0n up and down ring circuits on separate rcds trip x half ok on both trip x 5 ok on both less than 40 m/secs but trip x 1 on both rcds tripped rcds but no readings due to safety cut out on meter indicating 50 v ,have lost manual so not sure what this means but strange on both new circuits and new hlgh integrity board rcds would appreciate any views.

I'm a bit confused by this thread as it looks like it got mixed up with some trolling which has now been deleted, so I'm not sure if the original problem got sorted.

So, a couple of questions to the OP to see if progress is being made...
- can you clarify what the original results were? The quote above seems to say you were getting tripping on half x but not on 1x, which would indicate some sort of problem!
- I've not seen the tester you are using, but if it has a selector to choose the rating of the RCD under test, have you checked that it is set correctly (I guess you are testing a 30mA RCD)
- exactly how were you testing? At a socket / with other items plugged in / on the bars in the CU?
 

Reply to rcd testing in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
164
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
646
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
801

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top