Where were you testing the RCD/RCBO, at the device terminals or at the socket outlets downstream??
All RCD devices should be tested at the device terminals for your recorded values, and not at the extremities of the circuit. The circuit will/should have already been tested/proved via ELI, Continuity, Polarity and IR tests etc...
You are therefore only testing the RCD devices themselves for conformity, not the wiring...
that's not how we're taught at college........