Installed 1 x 40A-30mA rcd on 4 lighting ccts, went around the house switching things on to make sure all was ok, suddenly it started tripping,
disconnected all the ccts apart from the one i was concerned with as that was what was required to be protected, It worked untill i got to the kitchen and switched on the light, tripped the rcd.
Seperated all the neutrals, earths & phase conductors, IR test, was fine up to the kitchen, had some strange readings so left it out and went back down, reset the rcd and now it will only stay in when there is nothing switched on.
I was getting 153 Volts Phase to Earth, 77 volts Neutral to Earth and 230 volts from phase to neutral.
The earth voltage fluctuated by 10 volts with switching of loads.
Does anyone out there have some advice, would be much appreciated.
Have had to connect the house up to just MCB protection at this stage to allow them to see at night, will have to go back next week for the first fix on the bathroom upstairs do Ill remedy the situation then I hope.
Worst case scenario is running a new cct back to the board and isolating what is existing from what i have worked on to ensure my side of things meets the current regs.
Might point out in NZ we dont use ring ccts, one line back to the switch board for each cct.
Cheers
disconnected all the ccts apart from the one i was concerned with as that was what was required to be protected, It worked untill i got to the kitchen and switched on the light, tripped the rcd.
Seperated all the neutrals, earths & phase conductors, IR test, was fine up to the kitchen, had some strange readings so left it out and went back down, reset the rcd and now it will only stay in when there is nothing switched on.
I was getting 153 Volts Phase to Earth, 77 volts Neutral to Earth and 230 volts from phase to neutral.
The earth voltage fluctuated by 10 volts with switching of loads.
Does anyone out there have some advice, would be much appreciated.
Have had to connect the house up to just MCB protection at this stage to allow them to see at night, will have to go back next week for the first fix on the bathroom upstairs do Ill remedy the situation then I hope.
Worst case scenario is running a new cct back to the board and isolating what is existing from what i have worked on to ensure my side of things meets the current regs.
Might point out in NZ we dont use ring ccts, one line back to the switch board for each cct.