Hi all,

I have been to a job today to have a look. The customer is moving some stud walls in a ground floor flat and wants me to move the electrics within them and fix them temporary while other walls are built. My only concern is the meter box is outside and the 25mm tails and 16mm cpc are fed from a 100dp switch next to meter, about 10 metres to consumer unit all surface fixed in 50x50 trunking along the top of one of these stud walls. Customer wants to chase these cables in now, so do these require rcd protection?

many thanks
 
If 1, no additional mechanical protection or 2, earthed metallic covering or 3, buried at a depth of less than 50mm then yes they will need additional protection via a 30mA RCD.

522.6.6 refers.

Also they should have additional overcurrent protection via a switchfuse for example, as they are over 4M in length the DNO will not guarantee their service fuse.
 
If 1, no additional mechanical protection or 2, earthed metallic covering or 3, buried at a depth of less than 50mm then yes they will need additional protection via a 30mA RCD.

522.6.6 refers.

Also they should have additional overcurrent protection via a switchfuse for example, as they are over 4M in length the DNO will not guarantee their service fuse.

Lenny, How would you stand regarding Section 314 ie, To comply with these requirements the circuits of an installation should not be connected to a single RCD, as this could lead to loss of supply to the entire installation in the event of a fault on one circuit, clearly inconvenient for the user of the building.
Its just a thought, but the tails will be feeding the entire install. Or is this a case of the big red book contradicting itself ??
 
thanks Lenny. Thanks for reg number ill have a look.

is 4mts the maximum? ill see if theres a shorter route as the current route is a little odd. 30ma is a pain for nuisance tripping is a 100ma time delay rcd suitable or does it have to be 30ma?
 
Lenny, How would you stand regarding Section 314 ie, To comply with these requirements the circuits of an installation should not be connected to a single RCD, as this could lead to loss of supply to the entire installation in the event of a fault on one circuit, clearly inconvenient for the user of the building.
Its just a thought, but the tails will be feeding the entire install. Or is this a case of the big red book contradicting itself ??


I would try and avoid this type of situation in any way possible for exactly for the reason you give. I would try and offer the required mechanical protection and keep the cable with the prescribed zone as per 522.6.6 (v).
 
thanks Lenny. Thanks for reg number ill have a look.

is 4mts the maximum? ill see if theres a shorter route as the current route is a little odd. 30ma is a pain for nuisance tripping is a 100ma time delay rcd suitable or does it have to be 30ma?

4M is the max my DNO permit, others may differ.

522.6.7 refers to the use of additional RCD protection where 522.6.6 (i) - (v) cannot be met and states that.....an RCD having the characteristics specified in 415.1.1 should be used.

415.1.1 states that.....'the use of an RCD with a rated residual operating current not exceeding 30mA' etc etc.
 
You are only just assessing the job,so explain the requirements regarding the way they are installed. and what action you have to take for protection of those tails. and let him chose a method to comply

Try not to let the customer tell you what installation method is going to be used without you pre warning them of requirements
In the end, he can have whatever method he choses,the only restriction should be that, as long as your installation complies
 
Never have been a fan of burrying the main tails. I go along with Lenny. Dont think an RCD would be wise on tails. Try to convince the customer that for practical purposes the tails would be better trunked in say, MT4. Plus the switchfuse would be needed as said.
 
Last edited by a moderator:

Reply to rcd to protect tails? in the Talk Electrician area at ElectriciansForums.net

Similar Threads

  • Question
Yeh that’s my thinking. I have to supply the box so can order a bigger 3 phase option to give myself a bit more room
Replies
3
Views
696
  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
642
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
1K
  • Question
End of the day it makes no difference to you wht the outcome of the eicr is….so if concerned give it C2 or fi and put the report to the person...
Replies
22
Views
7K
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
947

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks