Hi all can anyone tell me the unacceptable trip current for a30ma rcd. I tested one on fri and the trip current was 24ma but i can't find anything in the regs to state what the minimum trip current is before its classed as nuisance tripping.

If anyone could explain how to carry out a ramp test as well I would really appreciate it,

Thanks once again

Chris
 
the Idn is the rated trip current ( 30mA ). as you know, RCDs should not trip at x 1/2 Idn. i.e 15mA.
 
Thanks Lenny, what does the 0.5 x ldn mean, I've seen it but don't really understand it? Thanks


When testing a 30mA RCD for instance, we are required to test at 0.5xIdN, 1xIdN & 5xIdN which equates to 15mA (30x0.5) 30mA (30x1) & 150mA (30x5)

IdN is the rated operating current of an RCD.
 
Hi Schoe

When carrying out a ramp test set you meter to the ramp test mode and make sure you have selected the 30mA range (Im not sure how its done on your fluke ) press the test button and the meter will start off by putting 15mA in and then increasing normally with new meters 1mA until it trips and the reading on your screen is the current that it has tripped at.

Have a look at page 91 of the on site guide for a little info on RCD's and test procedures!
 
Last edited:

Reply to Rcd trip current in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
791
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
631
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top