sirocco
Just been called out investigate RCD tripping on downstairs ring at my parents it just went in the early hours with no history. Have unplugged all appliances from the 10 sockets on this ring and switched all sockets off. There are no other appliances fed from this ring other than those plugged in via sockets. There are 3 other circuits protected by the same RCD in the CU ie Shower, Cooker and upstairs ring, these are all functioning normally and don't trip the RCD. I have substituted the downstairs ring MCB but the circuit still trips the RCD immediately when the MCB is switched on with nothing plugged into the sockets. My next step is to disconnect the ring, split the dead ring at the midpoint and test each half, but before doing this I removed the 2 CPCs for the ring at the CU from the earth bar and the circuit now stays on and doesn't trip. Before I plough on , disconnect the phase and neutrals and do dead circuit testing is there anyway that I can identify why the disconnection of the CPCs allows the ring to operate? Graham