Hi folks,
Hoping somebody on here can give me a little bit of advice. Just tested trip times on a 30mA 61009 RCD, greatest time at x1 was 24ms and at x5 was 28ms.
I know the regs state that at x1 under 300ms is needed and at x50 a reading under 40ms is required - but should the x1 reading be greater than the x5 - or is it "just one of those things!"
Thank you in anticipation of help!
BigGrilla