Hi

I have an issue with random RCD tripping. It happens at different times of the day and no obvious cause (ie particular piece of equipment).

All connected equipment has passed recent PAT test and IR on circuit looks ok (>600M PE).

A lot of the connected equipment has thermostat controlled heating elements - wax melting machines etc (it’s a beauty salon).

Had a thought that if a couple of RCD protected socket adapaters were put on the sockets and checked whenever it tripped, Does this sound like a reasonable albeit long winded way of narrowing down the fault??

Any other suggestions??

RCD Socket-Outlets
If you have socket-outlets which contain an RCD, it's important to ensure adequate discrimination has been provided. For example, if a socket-outlet containing a 30mA RCD is installed on the same circuit which is protected by another 30mA RCD at the consumer unit; it's possible that either of the RCD's will trip. Therefore, it's important to ensure discrimination is provided (delayed/higher value RCDs fitted at the source).

Earth-Leakage
Some appliances can 'leak' current to earth during use, which is known as an 'earth-leakage'. Often, the earth-leakage value is very small and insignificant on it's own, however if there are many appliances used which all contribute earth-leakage, the total value will increase and can trip a RCD (normally rated at 30mA).

RCD Testing
It's worthwhile performing tests on the RCD to ensure correct operation. This can include a ramp-test to determine the current required to trip the RCD and confirm functionality.
 

Reply to RCD tripping a mystery in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
545
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
988
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
921

Similar threads

T
Not sure how these things operate, but I expect a limit switch near each extreme position to tell the motor to stop. Have you got a wiring...
Replies
1
Views
172
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top