Hello, to everyone, would like some clues and ideas please, from obviously more experienced members on this forum.
Have attended the call out from customer, apparently his sockets don’t work. The board is old with plug in BS1361 cartridge fuses, as soon as I put the only one ring circuit fuse in it, then it trips the RCD which serves other 4 circuits, so I know obviously the fault is in the ring, wanted to do the full 3 step test on it but access in the board is terrible where you need to take the casings apart but they all imbedded sort of in the wall and stuff. It is inthe council flat. The only quick test in the board I done is line end to end which was fine, then with all the cables in their terminals I checked the continuity between them, I got the continuity between all of them on that circuit which is obviously wrong. Started going through the flat and opening sockets etc. all good, no works has been done, no nails through the walls, was wondering about squashed cable somewhere, finally found the offending part of that ring. It is a heating system which is taped of through FCU of one of the sockets,with boiler and all other associated parts: timers ,thermostatic valves, pumps,room stats connected one 12 way terminal block in one of those Plan S,Y,W systems and so on, as long as I disconnect that part of the ring by just taking the fuse out of FCU, everything is fine, I am not very familiar with the heating system wiring , that it is still to be learned, I suppose it could be anything you name it, so that where my question stands what you think could bewrong, it just seems that all conductors touching each other somewhere what could cause that. Obviously The customer is all happy that he is got power back on , but wants me to look further when I have time.
Thanks everyone reading it, and all you advice will be much appreciated, thanks in advance
 
Last edited:
Hopefully this has taught you that the first thing to do with a fault like this is to physically disconnect everything you can from the ring to eliminate faulty appliances, which seem more often than not to clear it! As for your heating system, I can't really answer you. I would probibly try and identify exactly what the fault is (i.e l/e or n/e) and then disconnect each componant individulaly until you clear that faulty.
 
With That Colosal wall of Text i managed,, I hope to work out that with the fuse removed from the heating system then all works.

You will need to IR test the items in the heating system by disconcting (keep earths conected) each item, Zone valve, boiler, pump etc.
you should narrow it down easy, probley quicker than it took me to read that wall of text! good luck
 
Thanks Richard for your reply, yes , that was the first thing I done, disconected everything, and just becouse I seen on the board fuse named heater I presumed heating system it was on its own circuit,but obviosly that was immersion heater instead, and I just later found that FCU with boiler and everything else taped of it....thanks...live and learn ah...
 
Disconnect the feed wire to the boiler itself then start testing........8/10 i've found it's been the boiler causing RCD tripping (or a component within it). If it solves the problem and the feed cable to the boiler is all ok then you need a boiler engineer to dive into the boiler itself.

IF with the boiler disconnect you still have RCD tripping then the fun starts as you've then got to go through the whole heating wiring system step by step (refer to post #4).
 

Reply to RCD tripping, advice in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
498
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
665

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top