I was called to a property the other day. Dual RCD board. One of the RCD's is tripping most mornings between 4am - 6am.

Check the board, only 4 circuits connected to that RCD, 1 socket circuit (upstairs sockets), 1 lighting circuit, smoke alarm circuit and outbuildings supply.

Tested all of the circuits seperatley, all readings above 5 Meg Ohms.

Couldn't find anything wrong anywhere, this has only just started to happen too, but it ONLY happens between 4am - 6am. Nothing plugged in thats on a timer etc.
Tested RCD out, and that seemed to be working as it should

Any ideas?
 
definitely suspect outbuildings. try isolating the feed ( L and N) and see what happens for a couple of days. have you ramp tested the RCD?
 
Ramp tested RCD, it was working fine

Outbuilds are now isolated, I'm seeing what happens there. Its the 4am - 6am that puzzles me, it never ever trips at any other time, and there's nothing plugged in in the outbuildings.

When we initially turned the power back on after testing, the security lights outside came on and worked fine.
 
there's also the possibility of a fault under floor. client gets up to go to the bog, pressure on floorboard causing fault on a cable with a nail in it????
 
just a process of elimination then. if the outbuildings being isolated solves the problem then investigate that circuit. if not go to plan B. just a case of tracing it down circuit by circuit, then point by point. hope that you're charging by the hour. :sunny:
 
As you've only got 4 circuits on the RCD and you've tried disconnecting 1 circuit, I'd be looking to disconnect another - yes not ideal for the client but it may be the only way.

Is it a dual board or could you fit RCBO's instead?
 
Aye, as chopper said and seeing as though you've pretty much tried everything normal - the fridge kicking in and out could be a real possibility.

Disconnect the fridge and if they moan about food going off...it'll be alright for at least 24hours.

Failing that, and what others have suggested...i think it could be the boogey man switching it off during the night.
 

Reply to RCD tripping, but with no fault in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
768
Ok I’ll try this when I’m down
Replies
4
Views
350

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top