if its a office you might not need all the circuits on an RCD. so can eliminate a few straight away. how is the lighting wired, also are there any outside lights.
 
Joe j

Don't follow your train of thought please explain further?

Still waiting joe j.


Just to clarify OP, I was asking where you are based in case someone reading this thread could pop in and have a look for you. Not quite sure how that fits with joe j :rolleyes2:
 
How many pc workstations are fed from the circuits protected by this RCD? If it's a 30mA RCD you can only run abot 10 workstations before it trips and thats without leakage from any other equipment. Have they recently added any PC's? There's only one real way to fix it and thats dead with insulation resistance tests at the CU with all the neutrals disconnected from each other.
If you're trying to fix it trial and error by removing bit's and pieces from the RCD then you be weeks instead of hours.

I hope the office is shut at weekends or you'll need a free night and a big torch!
Good luck
 
This thread is a week or so old, all this ground has been covered and the OP has been made fully aware of design leakage by lighting computers etc, the limitations of removing the RCD from circuits and what needs doing if it is done for fault finding purposes, also he has been made aware of the testing sequences and the quickest way to identify problem. As recently mentioned its just going around in circles.

note what hasn't been mentioned here is if the leakage is designed high earth then the RCD could be changed to a Main switch and a SI unit 30mA put up front of board, this recognises and ignore certain design frequencies and allows for a greater no' of computers etc.

In reply to Tonk a design allowance of 3mA per work point is advisable thus making a circuit only six workstations at max, 10 workstations leaves you open to the occasional nuisance tripping.
 
With regards to my SI-RCD unit suggestion, its may be a quick fix but only if it is high earth design currents, but the installations is poor by design and its this that should be addressed, with all the hours spent searching the fault, a few hundred quid to fit rcbo's and front end with main switch would be cost effective and also will identify the problem circuit if genuine fault leak exists.
 
Seems to be an IT high earth leakage thread!
I've I&Ted loads of Banks and virtually all of them had RCD sockets on standard ccts.
Made sense to me.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
RCD tripping dilemma
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
48

Advert

Thread statistics

Created
2BobSparky,
Last reply from
joe j,
Replies
48
Views
10,247

Advert

Back
Top