As a keen adult learner any help would be appreciated
I understand that an RCD trips when there is an imbalance detected between L and N.
If a 30mA RCD is monitoring several circuits (in a split board for example) and one of the circuits is protected by a 32A Type B MCB. I'm trying to understand what would happen in the following situations and would appreciate some help.
In a L-N short circuit the RCD would not trip but the MCB would when 160A passes through the MCB?
If a L-E or N-E fault then the RCD would trip before the MCB?
Any advice on fault finding a tripping RCD would also be appreciated