RCD tripping. Give me a clue! | Page 2 | on ElectriciansForums

Discuss RCD tripping. Give me a clue! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Yep, but if there happens to be 9mA leakage and your ramp test shows a pass at 22mA then you will leave a non-compliant RCDin service thinking it's okay.
 
Forget the torque driver, an earth leakage clamp meter would be more important.

You can't use an inline ammeter to check leakage current because it will only tell you what's going down the CPC, not what's being lost down parallel paths. The RCD doesn't monitor the CPC current so the test would be meaningless.

Good point! Can you recommend a suitable meter.

I accept that the RCD is looking at an imbalance between L and N. Isn't that difference also reflected in the main cpc?
 
I think many of the UK guys seem to use a Dialog earth leakage clamp meter which I believe is very reasonably priced. I'm sure someone will chip in with the exact model number for you.

Not all fault currents flow down the CPC, for example if an appliance has an IR fault and happens to be in contact with the kitchen sink then the fault current or a good portion of it will flow to earth through the water pipework and/or the earth bonding.
 
A common one is fridge and freezer compressors,these can test out OK but when they have run for a while and heat up they reveal a fault,that can be a real pain to find.
 
Do you not think 1.47 Mohms is a low reading?

Doesn't GN3 state 1Mohm is acceptable reading but anything less than 2Mohms requires further investigation.

Not sure why your testing with everything plugged in? Not sure what this achieves?

The chances are 1.47 Mohms is probably due to it reading through an appliance.

Remove the appliances, lamps, etc. and retest IR on each circuit, see if the readings improve (I guess they will).

If they do try PAT testing each appliance, if one looks dodge exclude it from circuit for few days see if that helps.

Trial & error only way forward if it's an appliance at fault
 
Yep, but if there happens to be 9mA leakage and your ramp test shows a pass at 22mA then you will leave a non-compliant RCDin service thinking it's okay.

You have to remember why I did the ramp test, which was to see if it was over sensitive rather than insensitive.
You've made me think though - I'm wondering why my assessors have never pulled me up for not switching off all unecessary circuits (eg.lights) when I do an Auto RCD test with my MFT. I tend to use the cooker circuit and switch off the ring(s) - doesn't do fridges any good! Is it because the standard auto test doesn't include a ramp test? When the tester leaks 30 mA does it take account of existing leakage?
 
When the tester leaks 30 mA does it take account of existing leakage?
Nope, the tester isn't that clever. If it applies a 30mA leakage test the actual leakage seen by the RCD will be the test leakage plus any other leakage from circuits and appliances.

Ideally you should disconnect all circuits and all loads from the RCD when ramp testing it.

It's good you're beginning to think about the bigger picture, it might help if you draw some circuit sketches of the possible fault paths and testing procedures.
 

Reply to RCD tripping. Give me a clue! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
554
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
992
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
924

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top