Forget the torque driver, an earth leakage clamp meter would be more important.
You can't use an inline ammeter to check leakage current because it will only tell you what's going down the CPC, not what's being lost down parallel paths. The RCD doesn't monitor the CPC current so the test would be meaningless.
Yep, but if there happens to be 9mA leakage and your ramp test shows a pass at 22mA then you will leave a non-compliant RCDin service thinking it's okay.
Nope, the tester isn't that clever. If it applies a 30mA leakage test the actual leakage seen by the RCD will be the test leakage plus any other leakage from circuits and appliances.When the tester leaks 30 mA does it take account of existing leakage?
Good point! Can you recommend a suitable meter.
I accept that the RCD is looking at an imbalance between L and N. Isn't that difference also reflected in the main cpc?