Can someone shed some light on a problem I'm having.
I changed a CU today as there were only 6 circuits they are all now rcbo's there was no rcd protection prior to that.
On the ground floor circuit the rcd test was x1@ 147ms and x5@ 23ms.
However now when the customer turns the heating on its fine and if they turn the hot water on at the same time it's tripping the rcd.
It is run from a fused connection unit and upon looking all looks good in the fcu.
It's a valiant ecotecplus 618 and the controller is a lifestyle lp522
I'm not a heating engineer but I may be missing something obvious.
 
Hi - just having nice cup of tea and reading this interesting post. Without seeing anything and tin hat on etc : trips when hot water asked for ... I'm liking the 2 port valve? As Lee says, there's likely 2 two port water valves near hw tank, one for supplying heating and one for hw. And a boiler with its own internal divertor valve and pump (sorry, I'm just imagining the set up there). Both the 2 port valves have moving parts, water and power connected and so may cause current leakage? I've not had a valve do this to me, but it would be any easy one to check if you're onsite. Anyway, I would ramp test the new RCBO to see exactly what current fires it and then start measuring the earth leakage current for the circuit - step by step. Hope that helps. Cheers, David.
Yes it has a hot water cylinder.
So im assuming that its leaking an earth somewhere. Which with the old Circuit breaker would not have been picked up as it did not trip the cb.
 
to perform a ramp test you need a MFT with that feature. on the megger ones, it's indicated with a triangle, like a steep slope road sign. you just connect to the RCD outgoing terminals with the circuit dissed, press "test" and it tells you the mA value that trips the RCD. it applies leakage currents in 3mA steps till the RCD trips.
 
to perform a ramp test you need a MFT with that feature. on the megger ones, it's indicated with a triangle, like a steep slope road sign. you just connect to the RCD outgoing terminals with the circuit dissed, press "test" and it tells you the mA value that trips the RCD. it applies leakage currents in 3mA steps till the RCD trips.
Ah right i use a kewtech kt65mft
 
OP. Think you need to start at the beginning again for this particular circuit What trip times are you getting on other RCBO's.

Start again with a fresh head, test circuit to FCU, dead tests, live tests, and then test house wiring to stat etc. Then having ruled them out, it could be something within the boiler, or zone valves etc.

PS you could test RCBO at CU with circuit disconnected to see how the RCBO functions independently. As telectrix, neutral earth faults can have an effect on trip times.
 

Reply to Rcd tripping issue. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
813
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
498
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top