Ok help before a pull out the rest of my hair got an rcd that trips when ring main breaker turned on got continuity but still trips when only live connected ant ideas
 
As the OP has disconnected the CPC and neutrals and the RCD is still tripping then logically there is a fault to earth on the line conductor.

This could either be a direct wiring fault such as damage insulation allowing contact with a back-box. Also reversed polarity on an appliance could cause the trip.
 
As the OP has disconnected the CPC and neutrals and the RCD is still tripping then logically there is a fault to earth on the line conductor.

This could either be a direct wiring fault such as damage insulation allowing contact with a back-box. Also reversed polarity on an appliance could cause the trip.
Stop repeating yourself, sign of old age.
 
As the OP has disconnected the CPC and neutrals and the RCD is still tripping then logically there is a fault to earth on the line conductor.

This could either be a direct wiring fault such as damage insulation allowing contact with a back-box. Also reversed polarity on an appliance could cause the trip.

Could still be a neutral to earth fault......his cct neutral would have been at line potential as he had it disconnected from supply neutral lol.

Due to no reponses.......I imagine he has thrown the RCD'S in the bin, took the money and wheelspan off the driveway into the sunset!!!
 
Could still be a neutral to earth fault......his cct neutral would have been at line potential as he had it disconnected from supply neutral lol.

Due to no reponses.......I imagine he has thrown the RCD'S in the bin, took the money and wheelspan off the driveway into the sunset!!!
A bit drastic don't you think.:tongue::tongue::tongue:
 
I'd try IR between all 6 conductors bunched in one crock clip and all the other conductors in the installation, checking cpcs first.

Does it trip if you only connect that circuit whilst having all other conductors disconnected or isolated?
 

Reply to rcd tripping on a ring main in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
295
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
277
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
354

Similar threads

My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
321
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
604

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top