A

Araman

I have installed a replacement (split load) cu fitted with two RCD's.

Prior to this I tested all circuits for polarity and insulation and found no problems, except for no (connected) cpc's on the lighting circuits and class I lights on the ground floor which are to be replaced with class II. (The cables used have a cpc but it is not used - please do not ask me why).

Only one circuit (first floor lighting, all with class II lights) will operate, the others all trip constantly. I have double-checked my wiring which seems sound.

I have had to leave the customer with the RCD's bridged to provide him with power and light overnight and must return at dawn tomorrow to try to sort the thing out.

Does anyone have similar experience to point me to where the problem may be?

Would it be more sensible to cut my loss and remove the RCD's and fit RCBO's in place of the MCB's or will these trip as easily?

All advice very gratefully received
 
sounds loike either a borrowed neutral or incorrect wiring of neutrals in CU. could even be manufacturers incorrect wiring. check all in CU 1st, then disconnect each circuit till fault disappears.
 
Have you checked for borrowed neutrals.

Have you checked that the RCD is wired correctly with the correct neutral bar.

I would be double checking the above first as you will have the same problems with RCBO's .
Iv made this mistake and it fryed my head trying to work it out!
Replaced the RCD all sorts and then had a BINGO Moment.
Easy to do, Really silly mistake but a good learning curve.
 
Have you done a ramp test on the rcd?

Ramp test says the RCD is tripping at 33mA. other RCD tests with the Megger (mft 1720) say the Rcd is defective but they both do trip on test. Surely it would be beyond a coincidence for both RCD's to be defective? Or am I being naive?
 
RCD's came installed in the cu. Would you believe it could be wired incorrectly?

I do not think I have missed a borrowed neutral but I will check.
Thanks
 
You think the factory where there made pays an Electrician to pre wire them?
Always check it mate, Its really easy to pop it in the wrong bar and have a head ache.
 
I do not think there are any borrowed neutrals but being an ignorant mechanical engineer lately retrained in the magical arts of electricity perhaps you can put me on the true path by telling me how to really check for such problems.

Many thanks for your help.
 
I do not think there are any borrowed neutrals but being an ignorant mechanical engineer lately retrained in the magical arts of electricity perhaps you can put me on the true path by telling me how to really check for such problems.

Many thanks for your help.


"I do not think there are any borrowed neutrals ..........perhaps you can put me on the true path...."

How can you say you don't think there can be any borrowed neutrals if you don't know how to look for them?

How old is the house?
 
Turn every thing off and turn each MCB on in turn, If it stays in(RCD) turn that mcb back off and keep repeating til you find the 1 that trips it,if they all do it the netural is in the wrong bar.
If its borrow it ll only be 1 that causing the issue and go from there<< thats how i would tackle it....
 
Not quite the response that encourages people to ask for advice Murdoch, even Newton admitted he stood on the shoulders of giants.

If ever you need advice on how to make a cogging gear for a 1930's gearbox, and how to make the tool to cut it, please do not hesitate to ask.

Each of us to his own.
 
Araman hes not having a pop hes just asking a question my friend.
Hes asking the age of the house because "Back in the day" Borrowed neturals was a common thing.
I think hes getting at if you put both the upstairs/down lights neturals in the same MCB it mite not trip the MCB and you l have found your problem.
But im guessing what he was getting at.
 

Reply to RCD tripping on new cu in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
864

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
682
davesparks
D
Ok I’ll try this when I’m down
Replies
4
Views
387

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top