Ramp test says the RCD is tripping at 33mA. other RCD tests with the Megger (mft 1720) say the Rcd is defective but they both do trip on test. Surely it would be beyond a coincidence for both RCD's to be defective? Or am I being naive?
Easy to check for borrowed neutrals....breakers/main switch off, disconnect one neutral at a time, megger between it and neutral bars, reconnect after test, test next one etc etc.
Araman I'm talking about the main earthing..if its too high it can give problems which an RCD will sense
For WayneL
1) Each cct should be discreet. The neutrals are commoned at the CU, by disconnecting a neutral from the board with the breakers/main sw. off that neutral should have no connection to any other. (Borrowed neutrals are not solely found on the lighting ccts) This is a simple test to find which ccts may be interconnected
2) An RCD test takes some current and diverts it to the earth path, if that path is of a high resistance the RCD will not trip as insufficient current will flow. Further some RCDs will detect a high earth and refuse to set. The OP has stated that both RCDs are tripping under load and yet will not trip when tested, as both RCDs are acting in the same manner it would seem that an external influence is acting here.
I hope that has explained my 'random' comments.