Good evening. Had a new consumer unit fitted a week ago, Paid over ÂŁ500+vat for a proteus 5+5 board to replace an old non-rcd board. Ever since it was fitted the right hand RCD has tripped in the middle of the night, between around 11pm and 7am, every night. This powers a socket circuit, an oven, hob and an alarm. The oven and hob were isolated at the control switches and the ring had nothing plugged in. In order to attempt to figure out what was causing the tripping I switched off the oven, hob and ring MCBs, leaving just the alarm on, it still tripped. I then disconnected the 3 neutrals for those circuits from the neutral bar and taped them up, it still tripped. I then disconnected the alarm, leaving nothing connected to the load side of the RCD, it still tripped. So I called the guy to report my findings that I suspect the RCD is a dud, as cannot see why else it would trip with no load connected. He turned up, used an RCD tester to make sure that the RCD tripped within range, which it did, said the RCD was fine and left. Guy who fitted it claimed there was a borrowed neutral somewhere, but really struggling to understand how the hell that could cause an RCD with no connection to the load side to trip. Can anyone here explain to me how the hell an RCD with no load connection can trip overnight like this?
Thanks, Lee.