Hi guys
this is my first post,so please go gentle.
i have recently finished a large domestic installation,which was put into service, after initial verification and all subsequent tests carried out with satisfactory results.
Now unfortunately I wasn't the last trade on site and now I have a problem with Rcd tripping once or twice a day( no set time of day)
I carried out Tests on RCDs results fine.
I tested A ring main circuit IR between L-N,L-E,N-E all clear but when I tested the disconnected Cpcs to neutral and got a reading of 4meg,also a voltage of 49V between the same Cpcs and neutral.
I left the circuit disconnected for 3 weeks (until able to return) and the RCDs have been fine( no tripping)
the installation is new and is TNC-S.
Ive spit the circuit into 2 radials,and get this same IR reading on each leg ( with the ring split at mid point)
Starting to do my head in now and wondered if anyone has any pointers for me before I get totally confused
thanks
this is my first post,so please go gentle.
i have recently finished a large domestic installation,which was put into service, after initial verification and all subsequent tests carried out with satisfactory results.
Now unfortunately I wasn't the last trade on site and now I have a problem with Rcd tripping once or twice a day( no set time of day)
I carried out Tests on RCDs results fine.
I tested A ring main circuit IR between L-N,L-E,N-E all clear but when I tested the disconnected Cpcs to neutral and got a reading of 4meg,also a voltage of 49V between the same Cpcs and neutral.
I left the circuit disconnected for 3 weeks (until able to return) and the RCDs have been fine( no tripping)
the installation is new and is TNC-S.
Ive spit the circuit into 2 radials,and get this same IR reading on each leg ( with the ring split at mid point)
Starting to do my head in now and wondered if anyone has any pointers for me before I get totally confused