Other option..."someone" has had sockets off entirely and messed up the terminations?
Line/Neutral wire come loose and touching an earthed back box?
Bad socket outlet?
ive run into this before with a cooling fan a neutral shorting against a box.
my poor apprentice had a fit trying to find the fault,
i told him what it was but had him find out where it was
tracked it down to the first junction box on the conduit run.
 
Also,if others have fiddled with socket fronts,especially decorators,don't just check terminations and cable bends,peep right down to see if cores have been pulled,cutting on backbox aperture,EVEN through grommet (if fitted!) They love doing their own version of insulation testing...
 
Hi guys here's an update'ive been on site today and done a thorough inspection and found that IR between earth and disconnected neutrals all fine(2 circuits 22 Meg all the others 299

One thing that has come to light is that the over head line has recently been changed to pme or pmb,not sure which .
But the overhead line now has a earth cable running from what I believe to be neutral to an earth electrode,which is about 30 yards from my incomer
Ive checked linked N & E at my supply and all ok,wondered if I was getting some sort of leakage to the suppliers neutral which is connected to an earth electrode in close proximity.
finally the property used to be a TT system and electrode still in the ground but not connected,also water supply in lead I think
oh and I've changed the Proteus RCDS for Hager
So wait and see!!!!!!!!!
 
No the overhead supplies PME N-E connection will have no affect on your RCD tripping problem. Depending on the Ra of the existing rod it might be a good idea to reconnect the rod to the MET. Don't bother if the Ra is way over 10 ohms.

22 Meg ohms equates to 22 million ohms, so you don't have a problem there either. So if the problem remains you have more checking and testing to do!!
 

Reply to Rcd tripping problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
559
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
993
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
925

Similar threads

Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
952
  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
617

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top