Firstly i'll point out that i'm the property owner and the installer of the majority of the electrical fittings in the building, including Main & E7 DB's.
now the history lesson... sorry, but it is relevant
property is 230 years old, I have owned it for 42 years. it was semi derelict at purchase, and i completed most of the rebuild including plumbing & electrics. (i'm not formally qualified in either trade)
building was wired to the existing standards (1978) at the time. and i opted to include E7 as the means of heating.
The system was checked and signed off by a qualified engineer, and the 'electricity board' engineer when meter was fitted.
The E7 DB connected to 6 individual points and 6 heaters of varying capacity were fitted. and the system worked well and reliably.
10 years after installation, i opted for a different heating system and the ESH's were removed, and that side of the system became redundant, though DB and points remained.
approximately 3 years ago the meter was changed, and, as far as i was aware, everything worked ok.
had the odd rcd trip over the years, don't you just love rogue tripping!, on 2 occasions traced to slugs in sockets in the conservatory would you believe... also damp in a JB .... apart from that no probs.

a month ago She Who Must Be Obeyed, decreed that we should have an ESH in the living room and another in the dining room (we won't go into the why's and wherefores right now, i'm just the labourer round here )
so.... ordered 2 nice dual input ESH's (Newlec, but Dimplex by another name), and duly fitted them....
i noted that they required a second (peak) supply into a fused DP point, so put them in as well.

connected the whole shebang up, all seemed great, until the next morning when i noted the rcd had tripped overnight., as E7 was still live, i isolated both ESH's and reset the trip, fine , stayed set ok.
switch on either ESH and the rcd trips.

well, seems i've cocked something up, so, check and recheck all ESH connections... all done by the book, and no obvious errors.

next i make up a cable to connect NSH direct to 24hr supply ..... works fine, no tripping, left for 2 hours for heater to warm up... all ok.

ok, the E7 DB is forty years old and running on 20a cartridge fuses and 60a mcb, (none of which are tripping by the way), so i fit a nice new DB with 100a mcb and 6 20a mcb's ... it would have had to be changed sooner or later anyway.

and we still have the rcd tripping! ....

nothing else, just the main rcd, and if the mcb's for each ESH are isolated then all is ok... and that is just removing live from the circuit, so what can be causing the problem? .... the only thing that has changed from when the old ESH's were removed to when the new ones were installed is the METER ...

going to need some help here guys....
 
as it stands, with the rcd tripped, the only live would be to the E7 cct, both live & neutral to the 24h cct would be isolated

No they wouldn't, if there's load on the E7 DB, that's why it's so dodgy. There's a path from E7 line, through the E7 load to the E7 neutral bar (which is now at 230V w.r.t earth), via the splitter block to the 24h neutral bar also now at 230V, through the 24h load to the 24h line. There's no circuit to supply neutral so none of the loads work and it all looks dead as a dodo, but every conductor in the installation is sitting at 230V via the loads. The resistance of a heater in series makes no practical difference to the severity of an electric shock. And there's no RCD protection.
 
No they wouldn't, if there's load on the E7 DB, that's why it's so dodgy. There's a path from E7 line, through the E7 load to the E7 neutral bar (which is now at 230V w.r.t earth), via the splitter block to the 24h neutral bar also now at 230V, through the 24h load to the 24h line. There's no circuit to supply neutral so none of the loads work and it all looks dead as a dodo, but every conductor in the installation is sitting at 230V via the loads. The resistance of a heater in series makes no practical difference to the severity of an electric shock. And there's no RCD protection.
yes, unless all the mcb in the E7 CU are off
[automerge]1573145473[/automerge]
I would get an electrician in to give the installation a thorough check. For your own peace of mind.
he was coming monday pm anyway... so (by law, i believe) i need to have it checked out for cockups and/or poor workmanship
[automerge]1573146087[/automerge]
how better to spend a wet afternoon ....
neutral split via new JB, new rcd fitted (80a) new tails where needed.
ccts are independant of each other now, each with own rcd.
what can possibly go wrong ? :)
thanks for your help guys, hopefully SWMBO will be nice and warm tomorrow, and i'll have lots of brownie points ....
will report back in the morning
 

Attachments

  • [ElectriciansForums.net] RCD tripping when E7 switches on
    e71.jpg
    96 KB · Views: 12
  • [ElectriciansForums.net] RCD tripping when E7 switches on
    e72.jpg
    90.6 KB · Views: 12
Last edited:
ok.... system working fine (well, apart from the fact that i failed to switch on one of the heaters ... doh) .... i checked them at 4 this morning (and switched on the one i left off last night !).
So, big thanks to you guys... saved me a lot of time and money, although i will still get it all checked by Mr Sparks on monday.
on reflection.... i'm a bit ----ed off with whoever fitted the new meter, and left the system in a dangerous state, i'm just lucky that i had no loads on the E7 side and the mcb was off. AND it cost me ÂŁ100 plus to remedy, on the plus side thankfully no-one got hurt....
thanks again
 

Reply to RCD tripping when E7 switches on in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
439
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
504
My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
358

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top