RCD tripping when earth core touched | on ElectriciansForums

Discuss RCD tripping when earth core touched in the UK Electrical Forum area at ElectriciansForums.net

K

Keefyjet

Hi,

As I understand, touching or cutting the earth core of a disconnected (via its MCB) circuit can cause an imbalance and an RCD trip – due to other working circuits connected to the same RCD bank.

So why doesn’t touching the earthed part of a working appliance (e.g. the chassis of a tumble dryer) cause the same imbalance and RCD trip?

Maybe I’m missing something blindingly obvious here – in which case please enlighten me.

Regards.


:21:
 
Are you sure it is earthed?

If your washing machine body is earthed and on a TN-C-S system the "Earth" and Neutral are effectively the same thing as they join together at the supply feed. You make a connection between your 'washers' CPC and the 'washers' neutral then it allows other circuits current an alternative path back (i.e. some current flows up the 'washers' neutral and down the 'washers' earth so passing the RCD and causing the inbalance).

There are a few assumptions there, the biggest being that you dont have a double pole 'washer' MCB and the neutral is isolated!
 
Disclaimer to this thread

Your understanding is appreciated
[ElectriciansForums.net] RCD tripping when earth core touched

This new technology is only just a recent introduction to us in Wales
[ElectriciansForums.net] RCD tripping when earth core touched
 
Touching an earth core shouldn't trip an rcd.
cutting the cables ( shorting the N & E) usually does

It depends what you touch the earth with, i'm confused aswell by the OP lol.

Stick your manhood on the earth, and you wont trip the RCD and if everythings in working order you won't get the thrill you're probably desiring.

Stick a line conductor on the earth, then you'll trip it.

Mr.Keefyjet what do you mean by touching the metallic frame of an appliance? I hope you're not suggesting, why should it not trip when you pick it up lol

I suggest reading up on earthing and bonding.
 
a pilot project in south wales introduced indoor toilets and bathrooms to a few select houses. when it was found that said toilets and bathrooms were being used to bath and shear the sheep, the project was abandoned in favour of underground housing, but those resourceful taffs kept coming back to the surface bringing up the coal.
 
Yes, the neutral is common but, as I understand it, the imbalance causing the RCD to trip occurs only if one or more of the other circuits under said RCD bank is/are in use? In other words if all of the circuits under the control of that RCD had no load the RCD wouldn't trip as there'd be no imbalance for it to detect?
 

Reply to RCD tripping when earth core touched in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
696
davesparks
D
  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
774

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top