Hi all.
I was called to a house recently where the occupier reported that when they turned the oven isolator off the RCD would trip.
So I tried it and that's exactly what happened. There was nothing switched on on the oven at the time. When the oven is on it works fine.
It is an integrated oven on a dedicated 16 amp circuit. Circuit tested fine in all respects and a ramp test on RCD showed it tripping at 24 mA.
They have to turn the isolator off when not using the oven as they have a son with learning difficulties who sometimes turns the controls on the front of th oven.
Any ideas what the cause might be?
Thanks.
 
Replace the DP switch with one which makes the neutral before the line and breaks the line before the neutral. I think MK cooker switches operate this way.

Understandable for a 3ph DB main switch for example.

However, this shouldn't in theory effect a single phase load. There isn't a difference in current draw, by switching line or neutral.

Unless the switch is faulty and is sending some current elsewhere.
 
Understandable for a 3ph DB main switch for example.

However, this shouldn't in theory effect a single phase load. There isn't a difference in current draw, by switching line or neutral.

Unless the switch is faulty and is sending some current elsewhere.

Beama talk about 'Double pole switching within the fixed wiring is known to produce a strange phenomenon whereby switching OFF a double pole switch supplied through an RCD can cause the RCD to trip.' in their RCD Handbook.

So there must be some substances to it.
 

Reply to RCD tripping when switching oven isolator off in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
350
Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
498

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top