RCD tripping when using loft socket. | on ElectriciansForums
Discuss RCD tripping when using loft socket. in the UK Electrical Forum area at ElectriciansForums.net
archee
Lincolnshire
Afternoon all,
I have an issue with the loft socket. When we moved the previous owners had a 2.5mm cable going up from the CU Via FCU however, the wiring was old and did not have earths(they cut them off).
So I decided to completely rip out the old wiring including unnecessary spur and put brand new 2.5mm cable connected to 16A mcb.
However, it trips the RCD but not the MCB. I don’t understand why.
I replaced the McB with the spare one I had laying around, was doing the same thing. Removed the mcb opened it up saw burnt marks on the inside. Ok I thought it might the MCB, so I received a new one today, same thing.
Checked previously:
All the wiring to the socket is correct!
Continuity check all fine!
Checked for Earth leakage with multimeter seems to be fine.
What else could cause this ? 😔
P.S I’m not using it for anything heavy just a 2A NAS server.
Have you carried out any IR tests?
You obviously have some sort of earth leak somewhere as this has only started happening since introducing the new cable with a cpc, as they cut it out of the old cable it wouldn’t have been possible to trip the RCD
Have you tried plugging something else into the socket? You might find that you have a fault appliance
No
No it doesn’t trip anything when nothing is plugged in. I also used the same cable and out it (just to test) on another 20A mcb and it worked fine.
You misunderstood what I said
Try and plug something else in. Grab your kettle or anything and plug it into this socket. If it doesn’t trip then whatever you are plugging into it is faulty.
Reply to RCD tripping when using loft socket. in the UK Electrical Forum area at ElectriciansForums.net
L
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Which rcd is it? Is it one for everything, one for a few circuits?
