RCD tripping while Zs | on ElectriciansForums

Discuss RCD tripping while Zs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

N

nicsin02

Hi guys, what would cause an RCD to trip when carrying out a Zs test, it is a lighting circuit in a new build house and I have it on the "no trip" setting and it still trips the RCD, the RCD itself passed the RCD tests and the IR is 800Mohms so that's fine, I even even replaced the RCD but the problem still exits, just a note it is a dual RCD board with each RCD protecting 4 mcb's and all other Zs test are fine its just the lighting circuit, any ideas guys, thanks in advance
 
"no trip" unfortunately doesnt mean what it says. certain rcds and test meters are incompatible for rcd testing on any scale.
 
It wasn't actually myself doing the testing it was the tester from my old company that fned me to see if I had any ideas, it is a robin ELI tester, he has been using it for years and he tested a few properties after the above mentioned and everything was fine so I don't think the tester is a fault
 
is the non trip test on your meter jut 2 wire, some older meters have to have three leads for the non trip test.
 
It wasn't actually myself doing the testing it was the tester from my old company that fned me to see if I had any ideas, it is a robin ELI tester, he has been using it for years and he tested a few properties after the above mentioned and everything was fine so I don't think the tester is a fault

If the guy was using a Robin yellow brick with D-lok (eg. KMP4120) it will not trip most passive RCDs, but the DC blocking method of 'No-trip' that the Robin uses is likely to be ineffective and trip a lot of modern sensitive RCDs, most RCBOs fall in to this later group.
 
Last edited by a moderator:
inb this case, the answer is to bridge out the RCD for testing. don't forget to remove the links after.
 
If everything else is ok, then generate your ZS value through calculation
ZS=ZE + (R1+R2)

Calculation is encouraged as an alternative to live measurements!
 
We had the exact same problem today doing a Zs test kept tripping the circuit breakers in the control panel. Some of the breakers were 2A and 4A when tried with a higher breaker it wouldn't trip.

Sent from my GT-I9300 using Tapatalk 2
 
If your doing a 2 wire Zs test and the RCD trips try swoping the leads over so E on line and L on Earth. That was megger's answer and it works.
 

Reply to RCD tripping while Zs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
856
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
980

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
390
My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
347

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top