We had the exact same problem today doing a Zs test kept tripping the circuit breakers in the control panel. Some of the breakers were 2A and 4A when tried with a higher breaker it wouldn't trip.

Sent from my GT-I9300 using Tapatalk 2
The reason why your MCB rated at 6A or less trips is because your loop tester sends a current of around 25A around the circuit during the test. The MCB recognises this as an overload condition and will trip. To overcome this you need to change the scale setting on your tester from 20 ohms upto 200ohms and repeat the test.
Unfortunately the only way to prevent an RCD tripping under test conditions is to use a loop tester with D-lock facility. Under no circumstances should you 'bridge-out' an RCD as this in breach of the EAW & H&S regulations.
 
A clever person on here once pointed out that you can get Zs by having the main switch on, the RCD off and the MCB on. Then bridge between line-cpc at your light fitting (or wherever) and then Zs test across the open RCD.

Laurie
 
The reason why your MCB rated at 6A or less trips is because your loop tester sends a current of around 25A around the circuit during the test. The MCB recognises this as an overload condition and will trip. To overcome this you need to change the scale setting on your tester from 20 ohms upto 200ohms and repeat the test.
Unfortunately the only way to prevent an RCD tripping under test conditions is to use a loop tester with D-lock facility. Under no circumstances should you 'bridge-out' an RCD as this in breach of the EAW & H&S regulations.

sorry, you're incorrect. the current generated by the tester on no trip is mA, that's 1 reason why the readings are not always accurate.
 
We are talking about an MCB tripping here. Not the fact that we are using the no trip setting. The op was asking why an MCB was tripping, not an RCD. The no trip setting sends a reduced current around the circuit to prevent a sensitive rcd tripping during the test. If you refer to your literature or head over to the IET website this is explained.
 

Reply to RCD tripping while Zs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
332
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
859
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
983

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
390
My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
347

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top