Hi,

Got called to a jobs due to the RCD tripping on the downstairs ring, as soon as the MCB for the ring is turned on the RCD trips.

I didn't have long but I did some quick tests, R1+R2 was fine on all sockets so I split the ring about half way and did an IR test on each side of the ring and got 0.01 ohm on both sides.

I had to go to another job but I am back tomorrow.

Any suggestions for what may cause this? or testing
 
Either two faults, or, there is another interconnection in the ring (ie wired up like an "8", not a "0").

Edit: oops, too slow! :)
 
Last edited:
yep as murdoch said, then just take it nice and easily, me personally I like to just do old fashion and bell things out and then label so i know which things are where and then you can track the fault relitavely quickly and i just use the rcd as the main tester lol keep splitting and checking if its okay best way IMO
 
Well I had another look and I have seen nothing like it. I disconnected one of the sockets about mid way and checked the resistance of r1 on both sides of the ring, and both sides gave approx 0.51 ohm, I then disconnected other sockets and on a 13 socket circuit only three made a difference to the reading, a couple gave open circuit on both sides. Customer has decided that they want it all redone correctly as a ring as every job in the house has been done wrong and installed by the DIY previous owner who had no clue.
 

Reply to RCD tripping in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
455
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
406
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
708
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top