Hi
I was called to a job where the rcd was tripping after a power cut. I have tested the circuits connected to it and all ok. I have tried turning the consumer unit off and on but rcd stays on. Would a power surge when power is re-energize cause this.
Any suggestions would be helpful.
Thanks
Steve
 
Ok tested rcd seems ok. I meant when I turned the consumer unit off to simulate a power cut it didnt cause the rcd to trip that is why i was wondering if a power surge when power is re-energized could cause it to trip.
 
It depends what was all switched on during the powercut that might not have been on when you simulated the action.

fridges, freezers and whatever may have been on or off depending on the status of their thermostats.
The power coming back on may have surged and blown a lightbulb, which can trip an rcd.

RCDs are sensitive little things.

I don’t think there is a problem, but if it’s only one rcd for the whole board, accumulative earth faults etc.... I’d recommend individual rcbo for each circuit.
 
Hi - if I’ve understood correctly, your Customer has reported there was a power cut, following which there was a period where the RCD was tripping, but it then settled and now works and tests ok with no fault found in the installation(?) . I have had this behaviour reported where DNO was having network issues. I’ve never been on site to test when it was happening, but I think it may be down to their N momentarily flicking away from the local E as network switching is happening. Any signs of this behaviour now and all bets are off :) .
 
somtimes when rcd hasnt been tested with the button in a long time it can trip easy. when its feeding heavy load like cookers, showers etc. even a light bulb blowing can trip it. first turn off all breakers then power on rcd . then one by one switch mcb;s back on. in my experience replacing the rcd to new solves it 99% of the time. unless its an older property with really bad old wiring then better get your thinking hat on.
 
When you say the RCD tested 'ok', what did it actually test as? Trip times and ramp?
If the RCD tests fine and all IR tests are fine, along with an acceptable earth leakage test and the only problem is that it has tripped once after a power cut, then I would say your job is done.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Invergarry
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Rcd tripping
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
9
Unsolved
--

Advert

Thread statistics

Created
Steve1968,
Last reply from
HappyHippyDad,
Replies
9
Views
2,573

Advert

Back
Top