RCD tripping | on ElectriciansForums

Discuss RCD tripping in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Joined
Jun 1, 2020
Messages
624
Reaction score
113
Location
London
A neighbour in an apartment block in my road contacted me. They have an ML CU with two RCDs, which is about one to two years old. We had the power go off for a few seconds them come back on. I never noticed anything myelf as my lights were all off. Anyhow they contacted me saying they had no power. I went around finding one RCD had tripped. I switched on and all is fine again. They do have electric underflor heating and one electric wall heater. I was wondering why it tripped. Would a spike do this?
 
Potentially, yes. Similar thing happens at my in-laws' house, when they have power cuts (fairly frequent, as there's a persistant fault on the underground supply that the DNO haven't managed to fix).

If power is cut off or restored very sharply, then high frequency components are introduced to the usual 50Hz waveform. Cables such as twin and earth have inherent capacitance. As the frequency of the waveform goes up (due to the sharp bits in the waveform due to the fault), the capacitive reactance (Xc) goes down, leading to leakage between live and earth. This can be detected by RCDs, which then trip.

It happened once while they were on holiday a couple of years back. Lost all the stuff in their freezer. :(
 
Potentially, yes. Similar thing happens at my in-laws' house, when they have power cuts (fairly frequent, as there's a persistant fault on the underground supply that the DNO haven't managed to fix).

If power is cut off or restored very sharply, then high frequency components are introduced to the usual 50Hz waveform. Cables such as twin and earth have inherent capacitance. As the frequency of the waveform goes up (due to the sharp bits in the waveform due to the fault), the capacitive reactance (Xc) goes down, leading to leakage between live and earth. This can be detected by RCDs, which then trip.

It happened once while they were on holiday a couple of years back.
whitch is why our freezers are on a RCD free circuit.
 
Potentially, yes. Similar thing happens at my in-laws' house, when they have power cuts (fairly frequent, as there's a persistant fault on the underground supply that the DNO haven't managed to fix).

If power is cut off or restored very sharply, then high frequency components are introduced to the usual 50Hz waveform. Cables such as twin and earth have inherent capacitance. As the frequency of the waveform goes up (due to the sharp bits in the waveform due to the fault), the capacitive reactance (Xc) goes down, leading to leakage between live and earth. This can be detected by RCDs, which then trip.

It happened once while they were on holiday a couple of years back. Lost all the stuff in their freezer. :(
I assume this would happen to an RCBO?
 
whitch is why our freezers are on a RCD free circuit.
I know someone who did this. The fridge/freezer is on its own circuit back to the CU on a simple 3A or 6A mcb. He said the freezer had no metal parts that a user could touch, so from a users point of view was double insulated not needing an RCBO or RCD.
 
Potentially, yes. Similar thing happens at my in-laws' house, when they have power cuts (fairly frequent, as there's a persistant fault on the underground supply that the DNO haven't managed to fix).

If power is cut off or restored very sharply, then high frequency components are introduced to the usual 50Hz waveform. Cables such as twin and earth have inherent capacitance. As the frequency of the waveform goes up (due to the sharp bits in the waveform due to the fault), the capacitive reactance (Xc) goes down, leading to leakage between live and earth. This can be detected by RCDs, which then trip.

It happened once while they were on holiday a couple of years back. Lost all the stuff in their freezer. :(
Would the new SPUs solve this?

[ElectriciansForums.net] RCD tripping
 
There is documented that a fridge freezer should be put on a separate circuit ( using a split CU. One bit of the CU for RCD protection and one without for such items.

i have a freezer in the farage and fitted an rcd which tripped when I plugged tools / lawnmower in.

interestingly, this didn’t happen using an RCD’d extension cable on a socket on the same circuit.
 
our set up is 40A MCB (not RCD) in CU with 6.00mm T/E to sub in garage. RFC in garage (freezers, my bench, etc.|) . external IP66 RCD sockets for mowers etc.
 
Would the new SPUs solve this?
Not necessarily. SPUs will chop the tops off excessive voltage peaks, but as happysteve explains, what tends to trip RCDs during spikes and brownouts is not the voltage itself but the sudden changes in voltage (dV/dt). The high rate of change causes high peak currents to flow through any capacitance to earth such as within interference suppressors, which the RCD detects as leakage (which technically it is.) Clearly if there is a high peak voltage with a high dV/dt, then the SPD might reduce it to the point where it doesn't cause a trip.

a freezer in the farage
Did you mean a greezer? A greezer in the Farage is worth...?
 
I know someone who did this. The fridge/freezer is on its own circuit back to the CU on a simple 3A or 6A mcb. He said the freezer had no metal parts that a user could touch, so from a users point of view was double insulated not needing an RCBO or RCD.

But did the cable supplying the freezer socket need RCD protection?
 
But did the cable supplying the freezer socket need RCD protection?

mine don't. all cabling in garage is surface. not as neat as maybe, but it works.
 
Not necessarily. SPUs will chop the tops off excessive voltage peaks, but as happysteve explains, what tends to trip RCDs during spikes and brownouts is not the voltage itself but the sudden changes in voltage (dV/dt). The high rate of change causes high peak currents to flow through any capacitance to earth such as within interference suppressors, which the RCD detects as leakage (which technically it is.) Clearly if there is a high peak voltage with a high dV/dt, then the SPD might reduce it to the point where it doesn't cause a trip.
I'd been pondering this for a while and had come to the same conclusion... I almost added some vague thoughts along those lines but lacked the confidence.

So what would prevent this - RCD tripping in due to transients - happening?

(1) less capacitance by design (shorter cable runs/few circuits)
(2) some sort of device that had capacitance to earth before the RCD, so the excess current would flow to earth there rather than in the circuits after the RCD in the event of a transient
(3) a choke (i.e. inductor) to limit the flow of current as the frequency increases

(1) is I guess something to consider when designing from scratch.

I suspect there's some sort of filter that effectively does some sort of combination of (2) and/or (3)... it's just not an SPD. It's the sort of thing you'd buy from RS or Farnell.
 

Reply to RCD tripping in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
385
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
966
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
499
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top