Doing a cu change and ring circuit is tripping the rcd. was working ok before on a non rcd breaker
any ideas what might be causing this.
any ideas what might be causing this.
I do and I've already given you a clue. I'll have to come back with the answer later though.still dont understand if ir test shows dead short L-N why would this not trip the breaker
You need "permission" to remove a danger when you're doing a CU change? It's a requirement of doing a CU change that the circuits are safe to be connected to the new unit. Your circuits are not safe by dint of a borrowed neutral. This issue could have been 'fixed' in a trice by simply putting all the lights on one MCB. Not ideal, but safe and would have taken you no time at all whilst wiring up the new unit.yes it will be reported to the client and rectified once i have permision
still dont understand if ir test shows dead short L-N why would this not trip the breaker
using a megger mft 1552 dont think it has another range