Should the rcd trip everytime if somebody had softly touched the live core of a cable? Or does it depend on wha current is flowing?
 
Rcd monitors imbalances line to neutral and if a live conductor is touched and 30mA (or less in most cases) flows away from the return path (neutral) it will detect the imbalance and trip. It's what its designed to do.
 
Yea I understand, so it will trip either below 30mA and above 30mA, soo when the RCD test is done at half it's rating why doesn't it trip isn't that 15mA then?? As that would be an imbalance is at correct?
 
Last edited by a moderator:
As Paul M has said the coil in the RCD moniotors the flow of the Line and Neutral conductors.

If either conductor flows to earth it will put the coil out of balance and trip the unit.

The amount of imbalance differs on each RCD but up to 15mA it should not trip but anything after that its down to each RCD.

That is why a series of tests are performed to make sure that the unit will trip out in the specified time.

That is for a BSEN RCD 300m seconds and a BS RCD 200 m Seconds.

Only a Ramp test will tell you at what stage the unit trips and it will record the mA it trips at!

If you softly (whatever that is ) touch a uninsulated live conductor and you are earthed the RCD is doing its job but the cable should have least insulation on it !

I hope this helps!!
 
basically,m yes. the trip threshold is set at 30mA as that is considered to be a level of current passing through your body that won't kill you.
 
Yea that a lot better thanks. Well the person was standing on a concrete floor while they touched it and they said it didn't trip. Would the concrete floor have anything to do with it?
 

Reply to Rcd tripping in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
284
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
786
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
383
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
681
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top