Can anybody help... Went to a job Friday where apparently RCD is coming out once every couple of nights. The rcd covers 4 circuits which are sockets, sockets, heating and outdoor shed. I have carried out a blanket test and I am getting a reading of about 20M This is with loads conncted apart from 2 neon extension leads which if connected brings it down to 0.39M.(still to high to cause tripping). I have also done a ramp test on rcd and it comes out at 23mA. Finally put clamp meter around tails serving rcd and with loads connected was still only getting 10.5mA of earth leakage. Thanks for any advice.
 
Can anybody help... Went to a job Friday where apparently RCD is coming out once every couple of nights. The rcd covers 4 circuits which are sockets, sockets, heating and outdoor shed. I have carried out a blanket test and I am getting a reading of about 20M This is with loads conncted apart from 2 neon extension leads which if connected brings it down to 0.39M.(still to high to cause tripping). I have also done a ramp test on rcd and it comes out at 23mA. Finally put clamp meter around tails serving rcd and with loads connected was still only getting 10.5mA of earth leakage. Thanks for any advice.

what kind of loads are connected
 
Washing machine, freezer, electric fence fed from shed, kettle, boiler. Even ran up heating but earth leakage still didn't go above 10.5mA. Did mention fitting rcbo's but if its an appliance breaking down this wouldn't help( just cause more expense).
 
From your testing the circuit wiring seems OK, therefore you are now heading for connected equipment with an intermittent fault, always a nightmare.
You probably need to do some investigation of the times and weather conditions when the RCD trips. If the trip is over night then it is only likely to be items that are running overnight.
Because some of the items are outside it could be water ingress, since you have 10mA already you only need another 13mA to trip it.
Could the electric fence be shorting when something pushes against the fence.
Freezers can be prone to tripping RCDs when old, less likely, but maybe you could run the freezer on an extension lead from another circuit for a few nights and see if the other circuit trips.
Did you run the ashing machine as these often break down to earth, but only when X item is activated, do they run the machine overnight?
 

Reply to RCD Tripping..... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
715
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
797
  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
506

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top