Evening everybody,
I’m wondering if someone wouldn’t mind answering a question for me about RCDs.

I had a water pipe burst behind my washing machine this evening, and once I’d isolated the leak I noticed the sockets had tripped. When I went to reset the breaker, I noticed that it was the RCD that had tripped, and not the MCB for the Ring Final Circuit which the washing machine is plugged into.
My question is ; why would the RCD trip but not the MCB? I understand that the MCB is there to protect the cabling in the event of fault current/overload, and that the purpose of an RCD is to interrupt the supply to reduce the effects of an electric shock. Would the RCD have tripped due to an earth fault such as the casing of the washing machine becoming live or water entering the socket behind the machine?
Thanks in advance and apologies for the lengthy post.

Regards
 
Yes, water has got in somewhere and created leakage path(s) to earth. Plain water is conductive enough that a wet fitting could have sufficient earth leakage for the RCD to detect. However, to trip the MCB would require a leakage path in the order of 500 - 1000 times lower resistance, which probably would not occur even with a socket outlet submerged in water.
 
with two units in a series arrangemant the fastest one trips first,
once that has tripped then there is no reason for the second one to trip
so it's purely a speed issue.
No it's a case if the water not producing a low enough resistance for fault current to flow, enough to trip the circuit breaker.
 
with two units in a series arrangemant the fastest one trips first,
once that has tripped then there is no reason for the second one to trip
so it's purely a speed issue.
Sorry dmx gotta disagree. They are 2 different devices offering 2 different functions. RCD provides earth leakage protection and a MCB overcurrent protection (Whether overload or short circuit).
 
Yes, water has got in somewhere and created leakage path(s) to earth. Plain water is conductive enough that a wet fitting could have sufficient earth leakage for the RCD to detect. However, to trip the MCB would require a leakage path in the order of 500 - 1000 times lower resistance, which probably would not occur even with a socket outlet submerged in water.
Thanks Lucien, will it be okay to leave the appliance/ socket to dry for 24hrs and the plug back in and try using it?
 
No it's a case if the water not producing a low enough resistance for fault current to flow, enough to trip the circuit breaker.

Woah, not so fast my friend. There is water involved, so there is going to be an earth fault. The reason the RCD trips first is because it is designed to trip within 40ms of a fault occurring.... way faster than any breaker or fuse will ever respond.
 
NO, A MCB will trip with an earth fault, but not when it is also protected by a RCD as the RCD trips too fast.
An mcb will require a much higher earth fault current to operate than an RCD. An RCD will only require a fault current of milliamps to operate whereas and mcb will require tens of amps over it's rated current, a current a 'wet' fault is unlikely to generate. However, yes, RCD trip times are faster than mcb times unless very high fault currents are involved.
 
Thanks for the responses guys. I understand that once the RCD had tripped the MCB wouldn’t trip, however what is the theory behind the RCD tripping? Would it be that the water had shorted between L-E due to its high conductivity?
 
NO, A MCB will trip with an earth fault, but not when it is also protected by a RCD as the RCD trips too fast.
An mcb operates in 2 ways, thermal overload and high current short circuit.
If the earth leakage path resistance is to high then then there will be insufficient current to trip the short circuit mechanism of the mcb. The mcb will only trip if the earth leakage current is high enough to operate the short circuit mechanism. Or if the thermal mechanism experiences a high enough excessive current flowing for a long enough period of time (depending on the type and rating).
A rcd however is designed to monitor current imbalances between L & N, so a much lower resistance earth leakage path will be enough to create a detectable imbalance (sensitivity depends on the rating of the rcd) to operate this device.
So in the op's scenario the small earth leakage caused by the water created a low enough resistance path for there to be a detectable imbalance for the in service rcd to operate first. If there had have been a "short circuit" then the mcb could quite possibly operate before the rcd.
 
Last edited:

Reply to RCD vs MCB trip in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
406
  • Question
As you said in #9 get an electrician involved. The information you are giving is not clear as you do not understand what is being asked which...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top