Hi everyone,

Quick question can you fit an RCD without any neutral connections?

If I have a 3 pole circuit breaker which has all 3 poles terminated with a 3 phase supply (L,L,L excluding neutral or earth) on the primary side and I am using only 2 phases on the secondary side (L,L) to create a 400v supply to a transformer, can I connect an RCD to this breaker?
 
If the DB has a matching 3P RCBO at a sane price that is the simplest solution.

Also fitting the 3P MCB and 4P RCD as if a full 3P+N load is needed, and just using Lx & Ly for the single 400V load is perfeclty reaonable and ensures the RCD works as intended. If in the future you need any other use, it is ready to go.
Thanks for your detailed explanation and response
 
The distribution board has 3 phases coming into it and is terminated to a 3 pole circuit breaker, but on the secondary side we are only using two phases. So wanted to know if I can connect an RCD to monitor the 2 phases.
In the past have seen a resistor,(100k or 100? ohm)connected between one phase and N on a 4 pole rcd so that the test button will work as normal and the unit will operate on 1,2 or 3 phases.
Regards,S
 

Reply to RCD without neutral 2 phase supply in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
Replies
4
Views
660
  • Question
<= This The RCD looks at any current imbalance between the cables routed though it, if N is not used then no current so it matters not from a...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top