J

Just

Hi, When I test socket ring x 1 I get 44ms and when I x 5 I get greater than 25V touch.. Zs is 0.53 and Ze is 0.17, IR is low 25M. Any ideas greatly appreciated
 
Think there was a thread on this just the other day, but tbh can't remember what was said,but if you are lucky someone might be able to link you to it. What tester is it - does it say anything about "greater than 25V" in the manual?
Have you tried putting another rcd in to see if you get the same result?
 
Hi thanks, I checked the manual and it just says touch voltage too high and that old chestnut 'requires further investigation' which to be fair it does! The meter which is a Socket&See was calibrated a few weeks ago. Any other circumstances would start testing but as the x 1 was 44ms surely there must be a fault with the rcd? As you say test with another. A poor IR wouldn't have anything to do with it would it?
 
Hi thanks, I checked the manual and it just says touch voltage too high and that old chestnut 'requires further investigation' which to be fair it does! The meter which is a Socket&See was calibrated a few weeks ago. Any other circumstances would start testing but as the x 1 was 44ms surely there must be a fault with the rcd? As you say test with another. A poor IR wouldn't have anything to do with it would it?

Can't see how a reading of 25MΩ could have anything to do with it tbh. Is it an rcd protecting several mcbs? Have you tried it with the other circuits turned off if it is?
 
Thanks farm, it's not the 44ms I'm worried about! The x1 is a fair reading which is why I am not sure x5 is greater than 25V touch. It's a TN system so it's under 400ms.
 
Test the Rcd with all loads off. Or switch off all mcbs and test the Rcd in isolation.
Many testers will give a greater than 25v touch voltage reading if the RCD doesn't trip within the required times.

Hope this helps.
 
Last edited:
Basically a RCD has to be tested 6 times.

Tests 1 & 2 are at 1/2 x the RCD rated current and are performed at 0 and 180 degrees of the cycle.

Tests 3 & 4 are at 1 x the RCD rated current and again performed at 0 & 180 degrees.

Tests 5 & 6 are at 5 x the RCD rated current at 0 and 180 degrees.
 
marcusone when you say all loads off do you mean nothing pluged into sockets or am i missing the point when i test my rcds ie ring main sockets there is nothing plugged into them hence i then carry out my secuence of rcd test with my tester cant understand were this 25v touch voltage is from is the tster detecting this interesd to find out as i have never came across this before
 
Don't understand why your meter is indicating a touch voltage >25V as this would be acceptable.

Touch voltage has to be <50V
 

Reply to RCD x 5 touch voltage too high in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
894

Similar threads

The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top