Hi, When I test socket ring x 1 I get 44ms and when I x 5 I get greater than 25V touch.. Zs is 0.53 and Ze is 0.17, IR is low 25M. Any ideas greatly appreciated
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss RCD x 5 touch voltage too high in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi thanks, I checked the manual and it just says touch voltage too high and that old chestnut 'requires further investigation' which to be fair it does! The meter which is a Socket&See was calibrated a few weeks ago. Any other circumstances would start testing but as the x 1 was 44ms surely there must be a fault with the rcd? As you say test with another. A poor IR wouldn't have anything to do with it would it?