25 v touch is for agricultural and i think construction sites , well it was for 16Th but not sure for 17Th now after malcolmsanford raised the question in the (switch heights on farms ) thread .
Malcolm , if you are reading this i will get back to you on this as soon as i have had a chance to check the current regs and gn3 !
As for your meter you can change this back to 25 V quite easily .
" Just " you say in your second post that your meter has just been calibrated , they probably finished calibrating it in 25 V mode and forgot to change it back before sending it out thats why you are now getting the odd readings .
17th Ed of the Electrical Wiring Regulations standardised the touch voltage requirement at <50V in all cases. Under the 16th Ed there was a special touch voltage requirement of <25V for Construction Site Installations and Agricultural & Horticultural Premises.
Thanks Mark that is what I thought. I don't have my 16th edition over here with me, but I had the thought that there were areas in the 16th that had 25volt touch requirements, but was unified to 50v in the 17th. I know that the new medical location was advocating the 25v touch voltage for certain zones, within the new amendment.
Thanks DP yes in that thread I saw that you mentioned the 25v in Agi and as I know you do a lit of Agi installs i was wondering if the 25v was a requirement from another set of standards. Cheers.
16th Ed,
Reg 604-04-08, page 150, section 604 concerned Construction Sites and this was where the 25V came in.
Also 605-05-09 mentions the same rule for Agricultural & Horticultural premesis.
Thanks all for the 25v explanation now how on earth do I change the thing back to greater than 50v for domestic!? Came up again yesterday on a x1 different property and won't complete the test. It's a DRC 430 RCD tester and as soon as I've got the cash it's going to be replaced! Worryingly there is nothing in the manual.
Looking at the instructions for the DRC 430 it says the test is stopped if the contact voltage rises above 25V so your meter is acting normally.
Although the BS7671:2008 regulations quotes 50V (although the amendment 1 now includes medical locations that do require 25V) I would be concerned if I did get a voltage above 25V as it means the earth is above 833R so in a normal environment it is indicating a problem (unless on a IT or TT supply).
Reply to RCD x 5 touch voltage too high in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Just introducing myself. I'm Dee, a DIYer with an off-grid solar system. I have a lot to learn especially since my system is not working. I'm...
The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...