I have just replaced a consumer unit and have one or two problems.
The first is taht on testing RCD trip times they will not trip. On x 1 tester reads 310ms but no trip, On x 5 tester reads 50ms but no trip. Thers are four rings with 2 on one RCD and 2 on the other and none of them trip.
The light circuits all work fine until I switch on the landing lights then both RCD's tripped. At the thought of borrowed neutrals I changed layout so all lights on same RCD but landing lights still trip that RCD.

Will investigate further to find fault on lights, but as this proves RCD's work does any body have an idea why sockets will not trip test ??
 
From the sounds of it, you problem could still be borrowed neutrals.

I suggest to start with, turn off all the MCB's and main switch etc and carry out a 250V IR test between the neutral bars, with the circuits still connected as they were intended.

If its flat, remove them one by one from the second bar until it clears.

That should identify which circuit is causing the probs.

Good luck, and take your time otherwise you WILL be going in circles.

Let us know how you get on.
 
Here is a tip which can save a lot of grief. When you install a new CU build it up, connect the tails, main earth and your bonding conductors. Install the RCD's and then power it up. Carry out the RCD trip tests, then you know that they work, and if they don't you can do something about it without having to strip down the whole CU. If you know they work, then after installing MCB's and wiring everything up it all goes t**s up you will know it is something you have done, or a problem with the fixed wiring. Same applies to RCBO's trip test before terminating the circuit into it.

Cheers...........Howard
 
Wasnt my help good enough then Howard? :D:D:D:D

I couldnt have put it better myself Jason. I have been where he is years ago, and that tip has saved me hours. An Elecsa assessor told me it in the days when i thought you had to do RCD tests on every circuit.:biggrin5:

Cheers...........Howard
 
Thanks Jason. I assume that will identify the fault on the light circuit.
Why are the RCD trip tests on x1 and x5 not tripping on any ring? The first RCD only has 2 circuits on it and both are seperate rings.
 
Well, difficult to say from here (other than sounding really patronising) especially on both RCDs.

Try removing a socket and shorting N & E.

Is your meter ok? Have you tested on other circuits with it? You didn't say.
 
Is your meter ok? Have you tested on other circuits with it? You didn't say.

Not done an RCD test with it for a week or so but it did just fine when I did and this is the first time it has given readings x1 310ms and x5 50ms but not tripped on any ring. Not sure what to do next ??
 
Not done an RCD test with it for a week or so but it did just fine when I did and this is the first time it has given readings x1 310ms and x5 50ms but not tripped on any ring. Not sure what to do next ??

I dont want to sound patronising or imply that you are stupid, but 1, is the install energised, and 2, are you testing the RCD on the load side?.
I have made both mistakes more than once.

What make of CU is it. if my memory serves me correctly i think Square D had links in their boards in the 16th days, and to make them 17th compliant you had to remove a link between the 2 neutral rails and one between the load side live of the main switch and the adjacent MCB, if you didnt then the RCD was effectively by passed.

Cheers............Howard
 
Last edited by a moderator:

Reply to Rcd's fail trip test on new consumer unit in the Talk Electrician area at ElectriciansForums.net

Similar Threads

Ok I’ll try this when I’m down
Replies
4
Views
288
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
449
davesparks
D
As a trainee, one of the things I've tried to focus on to deepen my interest in the world of electrics, is the space for creativity. I've...
Replies
0
Views
220
  • Question
A kettle boiling fish - thats your fault right there... or is it a red herring? :)
Replies
4
Views
2K
  • Question
Yea all out circuits were disconnected & Rcd ramped tested Think this will be the right way forward,with EL clamp meter Cheers have a nice Christmas 😎
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks