RCDs for fault protection in adibatic equasion | Page 2 | on ElectriciansForums

Discuss RCDs for fault protection in adibatic equasion in the UK Electrical Forum area at ElectriciansForums.net

Joined
Sep 26, 2023
Messages
6
Reaction score
1
Location
Uk
Hi all

Was looking in to the adibatic equasion as our company will not let us add on to a Ring circuit with 1mm cpc..

I want to give some evidence as to why it may not be an issue.

My question is;

If the circuit is protected by an rcd can I replace fault current in the adibatic equasion with 30ma as that is all the rcd will potentaly allow to flow down the cpc?

Thanks
 
Could you not add a fused spur to provide protection for the spur?
An mcb will always trip faster than an rcd in the magnetic(instant) part of the curve.
Its all about the let though energy ,how much current is flowing thought the cable an the time its flowing,this is what heats the cable and more importantly the insulation.
 
Could you not take an r1+r2 for the ring, add the proposed lengths for the extension, divide that by 4 for, add the Ze to get a theoretical Zs and establish a theoretical PEFC. Use fig 3A4 or assume that above a PEFC of 160A a type B 60898/61009 is going to go in <0.1 and then plug in your PFC and 0.1 to the adiabatic and get something smaller than 1.5, given I imagine a 6KA figure is substantially greater than the PEFC you're going to see?

Or maybe I am well out o_O
 

Reply to RCDs for fault protection in adibatic equasion in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
270
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
782
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top