View the thread, titled "RCD's in Domestic Properties" which is posted in Domestic Electrician Forum on Electricians Forums.
leep82
Just wondering, all my training was done towards the 17th edition so i have always known/installed RCD's were necessary in domestic installations.
My mum has recently moved house and when i went round to have a look, i naturally gave the mains a glance. TNC-S supply and a split load board with 100A main switch and 80A 30ma RCD. On the RCD protected side there is kitchen and house ring main, cooker and shower, and off the main switch, lights and boiler supply.
Is this common of earlier editions of the regs? Ive heard of sockets needing RCD protection prior to 17th edition but what about the installation as a whole as there will obviously be cables buried at a depth of less than 50mm which arnt RCD protected.
The reason i ask is that the installation looks relatively new and there is even harmonised colour cable used ( although i suppose this could have been additional work carried out at a later date than original install ), surely somebody wouldnt have installed this to current regs?
Sorry to muddy the waters but it doesn't comply with the current edition of BS7671 - additional protection by rcd should be recommended on an EICR.
That said I do agree that as long as it complies with 16th edition I wouldn't bother upgrading it just for the sake of it - it didn't suddenly become dangerous overnight.
only if the circuit cables on the non-RCD side don't comply with 522.6.101 in other ways. then it's a code C3.
As so many of my learned colleagues have already correctly stated, RCD's are not required in domestic premises other than for specifically highlighted purposes within BS7671. However, as a generalism I think you can safely say most houses will have cable buried less than 50mm in walls, circuits in bathrooms and sockets likely to be used to power outdoor equipment!
If you were doing an inspection these would normally be C3 observations although two can become a C2 --- if following guidance from the electrical safety first publication!
In this example from the OP, with just lights/boiler being non-RCD protected then a C3 seems appropriate in not meeting current regs and an upgrade recommended --- unless the boiler feed is to a socket likely to be used for outdoors and there's no supp bonding in the bathroom!
what should be considered 16th edition board supplementary bonding in place all tests comply to those laid out in Regs 2008 as amended, would be to risk asses the usage of the installation for example if its a rented property then the addition of RCD protection would be appropriate especially if its students that have been let loose from the family home , RCD's are not the be all and end all , that is why it is very important for the test reading to be with the readings laid out in BS7671 if an RCD fails the circuit needs to disconnect in the required time ,this is why i feel the item in the event of high Zs readings RCD protection is one of the remedial actions ,this should be removed , we should finding out why the reading are above the maximum permitted and rectify that problem for example a shower circuit 32 amp mcb r1r2 reading 0.86 Zs 1.39 , cable run approx 10 meters , stick an RCD on it it will be fine , no there is obviously an problem , its this sort of thing im on about
The sockets would need to be rcd protected anyway unless for a specific item of equipment - you're more likely to get a shock from handheld equipment plugged into a socket than from the socket itself.
Reply to the thread, titled "RCD's in Domestic Properties" which is posted in Domestic Electrician Forum on Electricians Forums.