Sparkz123

Hi,

I have a problem with 17t edition consumer unit (MK Sentry) on a TT system that has completely left me baffled. I'd be very grateful for an advice.

On the left hand side of the board I have a 100 amp main switch. Immediately next to that a 30ma RCD controlling 3 MCB's and 2 spare ways, followed by a second MCB controlling 4 MCB's and one spare.

If I test the3 left hand circuits the L/H RCD fails to operate, it also fails to operate when tested from the board. If I test any of the circuits controlled by the R/H RCD both RCD's trip. If I swap the RCDs around nothing changes, the L/H one fails to operate unless the R/H one is tested.

All my neutrals are connected to the correct connector blocks and there are no IR readings between the two blocks.

To leave the entire installation RCD protected overnight I swapped the main switch and L/H RCD's around, so the main switch was an RCD, but this failed to operate, even though it was fine when controlling the L/H circuits.

I'd appreciate any input.

Thanks,

Pete.
 
Disconnect all circuits from the board and carry out RCD tests with prods , see what happens , if all works correctly for both RCDs then its an issue with your wiring , or faulty RCDs ,
 
It may or may not be relevant here, but I recently installed an MK Sentry dual RCD board, where one RCD failed to trip on test. I had to leave the installation covered by the one good one as it was getting dark.
 
It may or may not be relevant here, but I recently installed an MK Sentry dual RCD board, where one RCD failed to trip on test. I had to leave the installation covered by the one good one as it was getting dark.

probably decided to trip at last and take the lights out.
 
It may or may not be relevant here, but I recently installed an MK Sentry dual RCD board, where one RCD failed to trip on test. I had to leave the installation covered by the one good one as it was getting dark.

That seems a bit of a coincidence, what was the outcome? Was it a faulty RCD or something else?

I'm confident that there are no shared neutrals, I have tested between the 2 neutral blocks and the readings were clear. It's not a new installation, I've just replaced an old board covered by a voltage operated trip. I'll disconnect all the circuits tomorrow and see what happens but I can't think of a wiring fault that could cause this. If it fails to work properly once the circuits are disconnected it's got to be a fault on the boards internal wiring, but God knows what.

Thanks everyone for the input.
 
That seems a bit of a coincidence, what was the outcome? Was it a faulty RCD or something else?

I'm confident that there are no shared neutrals, I have tested between the 2 neutral blocks and the readings were clear. It's not a new installation, I've just replaced an old board covered by a voltage operated trip. I'll disconnect all the circuits tomorrow and see what happens but I can't think of a wiring fault that could cause this. If it fails to work properly once the circuits are disconnected it's got to be a fault on the boards internal wiring, but God knows what.

Thanks everyone for the input.

Same thing, replaced board in brother in law's house, up front VO trip and re-wireable board, two new rings to give adequate sockets outlets in bedrooms and lounge, also to overcome lose of earth in lounge sockets. Come to test and one RCD won't trip. Faulty RCD. Also the mcbs wouldn't sit straight, and the factory wired neutral links came loose from the crimped lugs.

Horrible board, won't ever use another through choice.
 
Same thing, replaced board in brother in law's house, up front VO trip and re-wireable board, two new rings to give adequate sockets outlets in bedrooms and lounge, also to overcome lose of earth in lounge sockets. Come to test and one RCD won't trip. Faulty RCD. Also the mcbs wouldn't sit straight, and the factory wired neutral links came loose from the crimped lugs.

Horrible board, won't ever use another through choice.

was that a MK board by any chance?
 

Reply to RCD's Misbehaving in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
275
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
269
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

hI Gent's. I I can explain this spur line briefly, maybe someone can help me? Everything is Spur, no rings. Inside of the house and main fuse...
Replies
0
Views
303
  • Question
I misread it.
    • Like
Replies
13
Views
905

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top