Sparkz123

Hi,

I have a problem with 17t edition consumer unit (MK Sentry) on a TT system that has completely left me baffled. I'd be very grateful for an advice.

On the left hand side of the board I have a 100 amp main switch. Immediately next to that a 30ma RCD controlling 3 MCB's and 2 spare ways, followed by a second MCB controlling 4 MCB's and one spare.

If I test the3 left hand circuits the L/H RCD fails to operate, it also fails to operate when tested from the board. If I test any of the circuits controlled by the R/H RCD both RCD's trip. If I swap the RCDs around nothing changes, the L/H one fails to operate unless the R/H one is tested.

All my neutrals are connected to the correct connector blocks and there are no IR readings between the two blocks.

To leave the entire installation RCD protected overnight I swapped the main switch and L/H RCD's around, so the main switch was an RCD, but this failed to operate, even though it was fine when controlling the L/H circuits.

I'd appreciate any input.

Thanks,

Pete.
 
An RCD that fails to trip by its own test button or an MFT while installed but works OK on the bench or with all circuits disconnected, usually indicates an N/E fault on the installation downstream. This causes the test button current or MFT test current to 'miss' the N side of the RCD by running to earth. In your case it suggests a fault on the L/H group of circuits, which I recommend re-testing.

I'm guessing the L/H RCD trips when using the MFT to test the R/H one but not with the test button? If so, this corroborates it as an N/E fault, as the R/H test button doesn't cause current to flow in the CPC and hence doesn't influence the L/H one. But the MFT dumps the test current to the CPC, some of which ends up returning via the L/H RCD neutral and tripping it.
 
The old LN sentry range from the 80s and 90s were good , but this new stuff is not , the sockets get me , has anyone noticed how tight the terminal screw threads are , a customer had some for me to fit for him ...
 
Last edited by a moderator:
High integrity board by any chance?? I've seen them come wired wrong. Outgoing neutrals in wrong bars etc.

Have you got any dead shorts neutral to earth on the connected circuits? Could prevent the rcd from operating when testing.
 

Reply to RCD's Misbehaving in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
278
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
270
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
351

Similar threads

hI Gent's. I I can explain this spur line briefly, maybe someone can help me? Everything is Spur, no rings. Inside of the house and main fuse...
Replies
0
Views
303
  • Question
I misread it.
    • Like
Replies
13
Views
905

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top