I thought I was right I just needed another view to prove I`m right, I`m having a debate with a landlord over this, as I pointed out to him that the main rcd switch failed the cut out time meaning the portakabin my client is using is not compliant with the regs and he said I`m not changing the main rcd unit install another one to the portakabin, I said you cant do that it will conflict the other rcd
 
I thought I was right I just needed another view to prove I`m right, I`m having a debate with a landlord over this, as I pointed out to him that the main rcd switch failed the cut out time meaning the portakabin my client is using is not compliant with the regs and he said I`m not changing the main rcd unit install another one to the portakabin, I said you cant do that it will conflict the other rcd

You should not have 2 RCD's of the same value in series. If the main one has "failed" to test within the correct times then it should be replaced. Installing another one downstream is not a proper solution.
 
On rare occasions it can be prudent to have 2x RCD in series to give a measure of redundancy due to the somewhat fallible nature of the beasts.

But it would be something designed in from the start, not done as a way of getting around a failed RCD.
 

Reply to rcds in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
980

Similar threads

If the main DB RCBO is there to provide additional protection (as it most probably is), then no, as S type RCDs are not suitable for providing...
Replies
1
Views
1K
loz2754
L
Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top