hi guys, this is my first question so please be patient,


as part of a b-tech study i have to design a circuit and state the size of cable used, iam going wrong somewhere but where so here is an example.

Ib = 9000/230 = 40 amps (rounded off)
In = 45 amp RCD.

now this is where i sort of loose the plot

Iz = In/correctionn factors.
say for grouping (3 circuits) Cg = 0.7
say for thermal insulation Ci = 0.5 (thermal isulation the whole route) so

Iz =In/Cg x Ci = 45/.7 x .5 = 45/.35 = 128. and thats got to be wrong.

please help

peter.
 
The problem your design is causing is trying to run 9kW (a lot of power) through thermal insulation.

Regulation 523.7 "A cable should preferably not be installed in a location where it is liable to be covered by thermal insulation...."

It looks like your calculations are right, and this is why the above regulation exists - if we ran all cables through thermal insulation for their entire length, we would be using an awful lot of copper!
 
1 the design current Ib must be found first
2 the overcurrent device rating In is then selected so that In is greater than or equal to Ib

In > Ib

then the tabulated current carrying capacity of the selected cable cable It is given by

It > In/ca,cg,ci,cc
 
Your calculations are on the right track. Many a time Ci will create huge change in the cable size.

What is the load? Is it a fixed load?

If you can determine that the load is not subject to possible overloading then you can stick with Ib instead of In.
 

Reply to re cable correction factors in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
382
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
963
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top