hi all can some one please tell me what the differance is on a short between any of the wires

e.g.

56.5Kohms
0.68ohms
>99Kohms

what is the closest reading a cable can take before a trips on a short circuit? i no what im trying to say but cant really explain it lol
 
lol haha right.......

if a have a reading of 89Kohms on my megger reading between live and earth this mean there is a short!!!! correct

sooooo

when u test r1+ r2 and u connect live and earth at CU the reading will ussalyy be 0. something.

soo at what point does the rcd detect a short circuit e.g. 50ohms???
 
89,000ohms is not a short! 0ohms is! As Tel says apply ohms law, if you have a resistance between L and E of 89k then the current flowing to earth in a 230V circuit will be 0.0026A. That's never going to take out a MCB let alone a 30mA (0.03A) RCD.
 
Also you're talking at cross purposes. R1+R2 readings are continuity tests carried out at very low voltages and will give the resistance of a circuit from end to end. Shorts in a circuit are tested for using an insulation resistance test. The applied test voltage is much higher (500V) and will give you a reading in Mohms. 1Mohm = 1,000,000ohms or 1000Kohms which is considerably greater then the resistances you will get with a continuity test.
 

Reply to readings on a megger in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
135
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
915
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
That would depend on the instrument. On my old BM10 when you press & hold the button it just powers up the inverter circuits to generate the...
Replies
5
Views
411
  • Question
Blown blade type fuses aren't always obvious. Swapping identical ones over is often the best way of checking them.
Replies
2
Views
283

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top