My customer currently has a shed at the bottom of his garden. The shed is approx 70m from the house as it is a huge garden.
The shed has electrics going to it. They are from another shed 20m away on a 1.5mm cable. This shed is from a spur off a socket in the house on a 13A FCU. It is 2.5mm.
So basically we have a ring in the house. Spur off to a FCU. 2.5mm for 50m to shed 1 and then 1.5mm 20m to shed 2.
It has been like this for many years and they have plugged all sorts into shed 2 without any problems with voltage drop. The house is a TT and Ze is 15ohms at the house (don't know at the shed)
I have suggested it is wired properly. This would mean 10mm cable purely to meet the VD requirements (for lights), assuming max demand 16A for sockets and 1A for lights.
This just seems extravagant. I realise we cant use the argument 'well it's worked fine for years', but it has. I am saying this purely with regards the VD, not any of the other poor design which requires improvement.
What I'm getting at is...
1. Do you feel the 6.9V VD for lighting is too small?
2. Has anyone ever come across a situation in a domestic premise where VD has been a problem due to an undersized cable being used?
The shed has electrics going to it. They are from another shed 20m away on a 1.5mm cable. This shed is from a spur off a socket in the house on a 13A FCU. It is 2.5mm.
So basically we have a ring in the house. Spur off to a FCU. 2.5mm for 50m to shed 1 and then 1.5mm 20m to shed 2.
It has been like this for many years and they have plugged all sorts into shed 2 without any problems with voltage drop. The house is a TT and Ze is 15ohms at the house (don't know at the shed)
I have suggested it is wired properly. This would mean 10mm cable purely to meet the VD requirements (for lights), assuming max demand 16A for sockets and 1A for lights.
This just seems extravagant. I realise we cant use the argument 'well it's worked fine for years', but it has. I am saying this purely with regards the VD, not any of the other poor design which requires improvement.
What I'm getting at is...
1. Do you feel the 6.9V VD for lighting is too small?
2. Has anyone ever come across a situation in a domestic premise where VD has been a problem due to an undersized cable being used?